    Posted by Anthony Wright on January 15, 2026 at 5:31 pm

    Name and shame: GE National

    I’ve moaned in here about my solar setup frequently tripping and the general dissatisfaction I have with my installation and I’ve always avoided naming the company. Today I decided I’ve got nothing to lose by naming them as I’ve been asking them for help for the last 3 months and they are ignoring my calls, voicemails or WhatsApp messages.

    Just a few photos to give you an idea of where things just aren’t quite right.

    Plastic box for the meter and RCBO

    Two 30mA single direction RCBO’s when installation manual indicates 100mA bi.

    Bare copper on many electrical connections

    Armoured cable not earthed

    I’ll be sending pictures and information to NICEIC showing the standards of their work and I’m having to pay another company to rectify the work that GE National are ignoring my requests for.

    Malc Nuneam replied 3 months ago 22 Members · 21 Replies
  • 21 Replies
  • Anna Bale

    Member
    January 15, 2026 at 5:34 pm

    Wow that is a shocking installation!

  • Jeff Banger

    Member
    January 15, 2026 at 5:34 pm

    im no spark but it looks like it was just thrown at the wall, proper lack of pride in work

  • Edward Johnson

    Member
    January 15, 2026 at 5:35 pm

    Is that an Swa glanded off with a stuffing gland

  • Edward Clark

    Member
    January 15, 2026 at 5:36 pm

    good luck I have had to report NAPIT to UKAS for discrimination and breach of contract I posted some examples on here of a dodgy install and NAPIT have gone out their way to assist the installer avoid him he goes under DJH REnewables or Solar Electrical connections

  • James Foster

    Member
    January 15, 2026 at 5:37 pm

    Is NICEIC a solar standard. I thought that was for ordinary sparks there’s a different qualification for Solar installers ??

    Obviously they should be capable of a tidier job than that regardless.

  • Gregory Hughes

    Member
    January 15, 2026 at 5:37 pm

    shocking that wasnt a electrician fitted that so bad

  • Henry Jackson

    Member
    January 15, 2026 at 5:38 pm

    When your friends dad has a contact who can do it cheaper

  • Ian Darke

    Member
    January 15, 2026 at 5:38 pm

    Were they MCS registered and did you pay by credit card?

    The whole system needs to be ripped out and re-installed to required standards.

    Have you also checked the roof?

  • Shane Cox

    Member
    January 15, 2026 at 5:39 pm

    A Trustpilot review should get your problems fixed.

  • Edward Jackson

    Member
    January 15, 2026 at 5:39 pm

    That is truly awful … I may (or may not … you’ll never prove it guvnor’) done electrical work as an amateur in the past and it was always a million times better than that mess! That literally looks like a DIY nightmare. To think a supposedly qualified electrician did it .. and worse, signed off en EIC as compliant is quite literally, shocking. I’d be on to NAPIT or NICEIC, and possibly your local building control department.

  • Jack Williams

    Member
    January 15, 2026 at 5:40 pm

    Good luck finding someone who makes 100mA bi-directional RCBO’s. Finding 100ma normal RCBO are trying for single phase. We used to use HAGER 6 x the price vs 30ma.

    We only use 30MA bi-directional RCBO ‘s in a new CU board with split tails and we never have an issue with tripping.

  • James Mitchell

    Member
    January 15, 2026 at 5:40 pm

    Whilst it’s small beer at the side of pretty much all of this, can I just say a Dymo label printer costs next to nowt in the scheme of things and always, always looks more professional than Sharpie.

  • Jane Harwich

    Member
    January 15, 2026 at 5:41 pm

    Was this the cheapest quote or the most expensive?

  • Jessica Yorath

    Member
    January 15, 2026 at 5:41 pm

    I went through something similar with Eco Green Partners of clevedon and just settled out of court. MCS will just point you to relevant body eg RECC for contract or relevant building/electrical regs. They will threaten to revoke membership but never do, they are pretty toothless. The only way I fixed mine was to pay another company and sue the original ones for the costs. It took two years. Good luck

  • Joe Wild

    Member
    January 15, 2026 at 5:42 pm

    It’s crazy they clearly know what there doing but finish of product must be good cosmetically and that would have been the easiest and cheapest part to do pure madness

  • Jonathan Turner

    Member
    January 15, 2026 at 5:43 pm

    Apart from the tripping problem most of that wouldn’t worry me too much. I asked on an electricians forum about whether a 100mA RCD as specified some inverter manufactures would meet regulations and he answers were not clear cut. The exposed copper is aesthetically bad rather than a safety issue. Is a metal box for the meter and RCBO needed when fitted externally? Do you want an external metal box liable to rust?

  • Joseph Adams

    Member
    January 15, 2026 at 5:43 pm

    I normally moan at cable ties cut with side cutters leaving razor sharp edges, but that is probably the best part of that installation.

  • Kenneth Clarke

    Member
    January 15, 2026 at 5:44 pm

    And used the black as neutral although they did identify it lol could have used a 100ma RCD that is bi directional so would take the rcbo out of the equation but the circuits it fed would need to have 30ma protection down stream

  • Kev Phillips

    Administrator
    January 15, 2026 at 5:44 pm

    Using grey as the earth was the first way to tell this was fitted by someone who doesn’t have a clue, before looking at the rest of the rough as fuck install.

    Yes, you could argue it’s identified etc etc, but it’s day one shit that.

    Insulation not going through the gland on another picture,

    Not ideal to bash someone’s work but this is rough.

  • Lawrence Palmer

    Member
    January 15, 2026 at 5:45 pm

    I’ve never had luck with Rcd/ rcbo on inverters

    Solar hybrid nearly all the time is surface mount so use of Rcd isn’t generally required

    That said I’ve not really known hanchu to trip RCD/RCBO

    As for This install it’s rough, really rough

    Here’s one of mine for comparison of how a install should generally look